Energy meter vs IoTaWatt, three-phase, three-wire (delta)


#21

Going over this setup, I think its necessary to check “allow negative power” for the three mains while doing this experiment.

If that was not checked, note when they are changed so that we can disregard data from before then if need be.


#22

ok thanks. I will change now and keep it over night

negativpower


#23

Could you also assign:

Main1 phase A
Main2 phase B
Main3 phase C

Thanks


#24

OK. updated config. thanks


#25

Hi again,

So after 12 hours with following settings:

2803_outputs

Power looks like this:

Not sure how relevant at this stage but comparing kwh output from iotawatt vs meter last 24h and 12h it looks like:


#26

CI had my money on L1-L3 with the new settings, but now I’m looking at how accurate the L2-L3 is before the change. Just to be sure I have that right, before the change main2 was phase A, and main3 was phase B, is that correct?

Being more of a programmer than electrical engineer, we may have to stumble on the solution here, but I would like to understand the ultimate solution, and be able to produce a methodology for others to do this.

I’m assuming that you are getting the most recent data directly from the IoTaWatt, rather than using the influx integral function. I have had anecdotal reports of that not working quite right with negative numbers, and I believe that this measurement method can produce them. There will be a solution to that potential problem once the proper setup is identified.

In the meantime, I’m still scratching my head. Can you verify that the VT is connected between L1 and L2?

UPDATE; @Giraffe, are you following this? I’d be interested in your input.


#27

Hi,

Settings before last test was:

Main1 - B
Main2 - A
Main3 - B

VT is connected to L1-L2.

Data compared with my meter is based on summed values from kwh output from iotawatt to influxdb.

Very much appreciated help so far. I could most likely live with the previous setup, as all my individual circuits seems to be working fine (1kw - electric heating = 1 kw on the iotawatt, 3kw on the warmwater = 3kw on the iotawatt, etc), but would be happy to conduct more tests / configurations if this would be interesting.


#28

One interesting observation that might help with confirming VT location / orientation is:

When L1, L2, L3 is set to A
L2 shows positive watts, L1 and L3 negative

When L1, L2, L3 is set to B
L3 shows negative watts, L1 and L2 positive

When L1, L2, L3 is set to C
L3 shows positive watts, L1 and L2 negative.

Sum of watts on above 3 combinations is always 0.

Might be a longshot, but found it as an interesting observation.


#29

I agree that the previous setup seemed to give the right solution. I’d like to take a look at one more thing:

I’d like to retrospectively look at that data from 21:00 - 09:00. I’m curious if the allow negative values is the reason the L1L3 doesn’t work as I had expected. We can test this by defining an output as:

(I1main abs) + (I3main abs)

Then take a look at the sum of those values over the 21:00 - 09:00 period. I think it will be 64.


#30

Not sure if this was correct, but here goes:

Created output:

Result:


#31

Something is off there, the result still goes negative. Could you show the output definition in the setup output display?


#32

Think I put the absenergy and power on 2nd y-axis


#33

Thanks, I see the right axis now. I now realize that this can’t be done retrospectively. The algebraic sum of each main is converted to absolute value, which is not the same as converting each individual measurement to absolute value. So this doesn’t work. Sorry. it would have to be done by removing the allow negative values and running for awhile.

This is how I understand it to be setup:

image

So in the earlier period when L2+L3 were correct, L2 was assigned to phase A and L3 was assigned to phase B, which resulted in both referencing L1 for voltage, as the method describes. You only need two mains CTs, so any of these should work when added together (allow negative values off):

main1 phase A
main3 phase C

main2 phase A
main3 phase B

main1 phase B
main2 phase C

The individual circuits are basically single phase, so they should be:

L1-L2 phase A
L2-L3 phase C
L3-L1 phase B

If you could double check that this is how you have it and it works, that would be great. I wanted to lay it out for the next person that needs to do a three-wire system. Please get back and confirm the accuracy of the results.

If you choose the first mains option above, main1, phase A and main3, phase C, with the extra input from removing main2 you could connect CTs to L1-A and L3-C on that branch meter and the sum should match that meter.


#34

Excellent ! I will "re"configure my iotawatt and revert with results tomorrow. Again thx for all the support!


#35

Hi,

So after ~10 hours it looks like we are spot on kwh usage between iotawatt and my meter !

From 23:00 - 9:00 I have used 38kwh both on the iotawatt and the utility meter.

I used the following setting where I am using sum of kwh from L2-L3.


#36

Just following up to be sure this is working correctly. Does your energy meter agree with the IoTaWatt now?


#37

Spot on ! Everything works perfectly !