Calibration for two Australian VTs

As everyone down-under knows, I don’t offer a VT for Australia, and users are pretty much on their own. Fortunately, there seem top be two generally available 9VAC wall transformers. While users could easily calibrate the voltage, phase shift was unknown. Thanks to @KentW, I now have a sample of each and was able to measure the shift and generate table entries.

The two models are:
DCSS AC910. As I understand it this model was acquired from Radio Parts.
Powertech MP-3027. I understand this to have been sourced from jaycar.

First impressions are that the MP-3027 is heavier at 455g vs 327g for the AC910. My experience is that phase shift is inversely proportional to weight. The next significant observation is that the MP-3027 is efficiency level V while the AC910 is level IV.

Here are the numbers:
image

Absolute Shift - The shift of the direct transformer output vs the (more or less) pure sine wave of the line voltage.

IoTaWatt chan 0 - the shift as read by the IoTaWatt channel 0. This includes the shift of a 10uf capacitor in series with the voltage divider. At 50Hz, that’s about 1.75° and at 60Hz it’s about 1.43°.

So as foretold by the weight, the MP3027 has significantly lower shift than the AC919, but both are in a good working range. I have added both to the table file for next release, but anyone is free to download this table file tables.txt (2.5 KB) and replace your current table.

The table specifies both the 60Hz and 50Hz corrections, but IoTaWatt will use the 60Hz correction. The reason is that IoTaWatt also uses 60Hz corrections for the CTs, and the variation due to line frequency is similar making the match up better using the 60Hz numbers all around. Correction uses the net difference between the CT and VT. If you are using mostly solid-core CTs, it may be better to use the lower 50Hz phase correction, but with the ubiquitous SCT013, the difference is about +1° while the AC919 is about +1.4° and the MP3027 at about +0.7°. So less than +/- 0.5° is pretty good, especially considering that the CT shift varies over a range anyway.

I’d give the MP3027 four stars and the AC919 three.

When the new calibration rig is completed, there will be 50Hz values for the CTs as well, and I’ll change IoTaWatt to use the “P50” values when line frequency dictates.

2 Likes

Awesome. Interesting I have the Doss and my calibration is set at 20.81 using generic VT, measured when I set it up with a Fluke voltmeter so pretty close. I’ll put the tables in shortly to select the new settings. Thanks @overeasy

That’s why I like to have two or three samples to do a thorough job. Each transformer will be a little different, and the voltage divider resistors are .5%. The voltage reference shunt is 0.2%. And then my Fluke meter is 1% of reading + three counts. So your mileage may vary. That’s why there’s a fine calibration capability. Your number is 1% higher than mine, which is reasonable.

Like the carpenter said: “It ain’t a piano”.

In the download I think you have the wrong cal setting on the DOSS, it came up at 130ish volts, I notice the table file has cal 11.1, but in the table above you have 20.72.

Ive changed it in my upload.
Cheers.

ARRRGGHH!

Stupid mistake. I just double checked the other numbers. I’ll fix it in the morning. That’s a lot closer to the 20.81 that you had ( 0.4%) so in the same row/section of the ballpark, just a different seat.

Thanks for the oversight.

Table file linked above is corrected, and link replicated here: tables.txt (2.5 KB)

Has anyone experienced the AC920, which seems to be the latest VT available from Radio Parts?
They don’t appear to stock the AC910 anymore and have instead opted for the 2 amp version from DOSS.com.au
I’m yet to commission my iotawatt but I guess I’ll start from the AC910 base calibration and go from there…

If someone sends me a sample, I’ll measure the phase shift and add to the table.