CT phase angle config

Im not understanding the multiple CT phase angle values for some of the CT’s in the standard tables.txt files. ( i get the 50 or 60hz but not the multiple phase angle errors ) @overeasy please could you let me know how these variables are added - i ask because i have some discrepancies on a 600A class 0.5 CT which varies more or less considerably versus my utility grade device at varied % of CT capacity.

Look forward to your assistance

There are several things that contribute to phase shift in a CT:

  • Frequency - as you point out.
  • Primary current
  • Individual variation in manufacture and installation

The device tables address all three:

  • As you point out, there are different specifications for 50Hz and 60Hz. Thankfully there are no common power systems that use other frequencies.

  • For each frequency, there is an array of shift/cutoff current entries to deal with primary current.

  • The table values are the average of two representative samples of the device (typically after testing more).

As you can see above, this 200A CT varies from about 0.5° down to a fairly steady 0.25° in midrange.

Realistically, quality larger CTs, and 0.5% CTs, have relatively low shift. Moreover, shift isn’t really a big source of measurement discrepancy until the power factor get down below, say, .70. If you are having issues with accuracy as compared to another measurement source, you might first compare VA between the two. VA would not be effected by phase-correction. Graph+ does not have a direct way to access VAh, but if you plot VA over any time period, the Data Statistics will show VAh.

If the VAh are within acceptable margins and kWh is not, then you might suspect phase-correction as a source of the discrepancy.

Tx Bob . The explanation makes sense. I tried the VA comparative approach first and i am lower in the datasets i checked by about a factor of 1.19 ( example i get 168kVA where the other source is 200kVA ), ive double checked primary output and turns ratio. I must be missing something - any thoughts?

Well then your problem isn’t phase correction. Both because VA is off and because the variance is too great to be a power factor problem.

You haven’t provided much information, so how many guesses do I get? As I recall, you may be building your own hardware. If that’s the case, there are a lot of possibilities beyond the usual suspects. But that said, I’m gonna go for it:

As you point out, the ratio of 200kVA to 168kVA is 1.19. The inverse is .84. The ratio of 20:24 is .833. Is it possible your unit is configured as 24 Ohm burden resistors and the actual value is 20 Ohm?

How incredibly brilliant Bob, that is exactly correct! I will get that change implimented asap - seems the perfect fit to my issue. :wink: