ECS36600 600A Echun CT Settings

Hello!

I’m using a 600A (!) CT and would like to confirm my “generic” settings. I am in Australia (50Hz).

The CT is a split core Echun unit with standard leads and TVS diode:

  • ECS36600
  • 600A/50mA
  • Random codes: 2038, L59C

I found a similiar one in the tables:

{“model”:“ECS36400”,“mfg”:“echun”,“type”:“C”,“turns”:8000,“phase”:0.1,“p60”:[0.1],“p50”:[0.2,10,0.1]},

And so think I should use these settings:

  • Turns = 600/0.050 = 12000
  • Phase = 0.1 (?)

I’m unable to pre-test, so can you confirm these are the right settings?

Thanks,

Brett

Hi Brett,
The turns should be correct. In general, those larger Echun CTs exhibit very minimal shift, so 0.1 should be fine.