I happened to be looking at the real-time status update screen on my IoTaWatt yesterday. I noticed a very large imbalance between the two legs of my USA 240VAC split phase. The difference was about 2kW which seemed odd to me. So I dug a little deeperand saw that my Samsung electric clothes dryer was running, and it was the main consumer of power. However, since the heating element in the dryer is 240VAC, I would have expected to see a similar amount of power usage on both legs of my power. It turns out that my neutral wire for that circuit, which should only carry the difference caused by the 120VAC motor and electronic controls, was carrying ~19.5A (verified via a clamp on meter.)
After a little online research, I discovered that the heating element in these Samsung dryers can sag and make contact with the chassis. Since my dryer outlet is only a 3-prong style, the chassis is bonded to the neutral wire as per Samsung’s instructions. This explains how the current is getting on the neutral wire as well as why my wife says it is taking a lot longer to dry the clothes than it used to. The dryer should be drawing up to 5300W while running, but is only drawing about 2000W due to the heating coil being shorted to chassis. It most likely broke and sagged to where it is making contact with the chassis, so less than half the coil is actually heating up.
I have ordered a bunch of parts to refurb the 11 year old dryer, as it still works pretty well. The parts are cheap. I am also going to change the dryer outlet to a 4-prong style and will replace the dryer cord accordingly. This should make for a safer setup in the long run.
Just wanted to say thanks to @overeasy for making such a great product! I would have never known about this situation were it not for IoTaWatt!
Nice catch. While IoTaWatt is a good tool to diagnose problems like this, it’s not like it sends you a message that your dryer might have a short to neutral. I think very few users would be able to track that down. Nice job and thanks for explaining here for everyone to see.
The repair was pretty straightforward. I also replaced my dryer’s drum belt, roller support wheels, and tensioner pully. The pully was seized up, and the old belt had worn through the plastic pulley. I am amazed the belt did not shred.
No luck on changing over to a 4 wire outlet and power cord, though. Looks like when my house was built, they saved a few pennies by using 10/3 Romex without a ground wire. Just Black, Red, and White wires. Oh well! I should create an automatic notification if my IoTaWatt reports a large power usage discrepency between L1 and L2. This would help me find this issue if it were to happen again in the future.
Again, Thank You @overeasy for creating and sharing the IoTaWatt with the world! Such a great product.
My dryer is the same (old Maytag Neptune). The difference is that mine has a ground wire connected to the copper water pipes. I always felt comfortable with that setup not knowing that neutral was bonded to the cabinet ground. Now I’m not clear on why that is the case. Two things:
If for some reason the neutral were to break between the street and the dryer, any short such as you had could put the whole cabinet at a high voltage.
The code does not allow bonding of ground and neutral beyond the entrance panel and this seems to do the same thing. If I had a GFCI breaker on the dryer, I think it would pop.
Interesting case study. For an electric dryer, the heating element cycling on and off is normal, so the current signature will show large steps rather than a steady draw. What matters is separating the element from the motor and timer loads, since the motor is a much smaller, fairly constant component. If you log at high enough resolution, the duty cycle of the element tells you more about performance than peak current alone. I’d be curious whether the anomaly tracked with a specific cycle phase or appeared across the whole run.
The point about the neutral bond is worth taking seriously. If that neutral path is compromised, the cabinet can become live, and the water-pipe ground only helps if that path stays intact. A GFCI would likely trip on that kind of fault, so it’s a reasonable safeguard. On the current signature, separating the element steps from the motor and timer draw makes sense; the duty cycle probably tells you more about element health than peak watts. I’d also check whether any anomaly lined up with a particular part of the cycle rather than the whole run.
I know you keep up with current postings and are one of the most active forum members. At this point, since I no longer make or sell IoTaWatt units, I still check daily but only looking for where folks need help.
Bots, primarily from Russia, have been trying to establish accounts for the past year. That’s why I require approval. Used to be pretty easy to identify them as they used a registration IP from Russia or Germany. Lately, I suspect the bots have gotten better. The two you mention were not the typical bot profile, so I let them through. Not sure how you know they are ai generated responses, but the forum software does have new features to respond to posts using ai that is apparently trained with the forum contents. The two you mention seem to offer reasonable information, although seemingly responding unsolicited to older posts.
I’m not up to fighting with bots and ai posters given the low volume of problems reported these days. At some point I’ll just turn off new users completely and post a message instructing how to send me an email requesting entry, probably with some type of “are you human?” test.
Hope things are well with you. BTW/ I plan to dump most of my ESP32 project onto github over the winter for folks to do with as they please. Probably get some DIY interest.