I had no problem configuring inputs 0, 1 and 2, but when I try to configure any of the other inputs, there is no save button, only a Cancel button. How can I fix this? I tried cycling power to no avail.
Would you post a screenshot of the input with only the cancel button?
OK, two different problems here:
In the first screen, you have specified a generic CT but have not provided an acceptable turns ratio. Note the message “Range is 100 to 18000.
In the second screen, the name contains a blank. Valid names have upper case, lowercase, digits and the underscore “_” character. Note the message “Invalid name”.
Thank you for the prompt diagnosis. My Bad.