New Installation - Australia, Regional NSW

That’s only a rare occurrence, e.g. if I need to take the off-grid system offline for maintenance or something like that.

In any case the RED and WHITE VTs will still be on their respective phase and be unaffected.

It depends.

If the off-grid system is in grid-pass through (Utility First) mode, then the grid supplies the phase timing. The power is a straight pass through.

If the off-grid system is not operating in grid-pass through mode, then the off-grid system is supplying the phase timing.

Which is why the BLUE phase VT is supplied power from the output of the off-grid inverter - so that the phase timing it supplies is in alignment with whatever the source of the power is, be it a grid pass through or generated by the off-grid inverter.

This is why I went with individual VTs.

So if I did need to flip the transfer switch back to grid-only (e.g. for off-grid maintenance), then in that time, I can either simply change the VT settings for those circuits back to their original phase, or not be fussed with having incorrect data if the downtime is short.