Three-phase, Three-wire questions

Received the following inquiry via Email. Responding here.

I am evaluating IoTaWatt for detailed home energy monitoring in Belgium and would appreciate your advice before ordering.

My house is supplied by a 3-phase, 3-wire 3 × 230 V DELTA system, with NO neutral conductor. There is approximately 230 V between any pair of phases (L1–L2, L2–L3, L3–L1). Most individual household circuits are 230 V two-wire loads connected between two live phases, using different phase pairs. Circuit breakers are typically 20 A, with some 16 A and 32 A circuits. I also have Enphase solar microinverters and an ORES smart meter with P1 data.

I would like to monitor around 10–14 individual circuits (heat-pump water heater, washing machine, dryer, oven, dishwasher, heat pumps/air conditioners, etc.), preferably with 50 A CT clamps, while retaining the existing circuit breakers. I use Home Assistant and would like fully local energy readings (W and kWh).

Could you please confirm:

Does the current IoTaWatt hardware support this exact 3 × 230 V delta/no-neutral supply for accurate active power and kWh measurements, including individual 230 V circuits connected across any of the three different phase pairs?

For each ordinary two-wire phase-to-phase branch circuit, is ONE CT on one conductor sufficient if the correct phase-pair reference is selected?

Can the derived-reference method use a single 230 V phase-to-phase voltage transformer in this situation? Which specific EU/Belgian-compatible voltage transformer(s) and setup would you recommend? Would direct voltage references be preferable?

How many of the 14 CT channels would remain available if I also wanted to measure the total three-phase supply? Would two CTs on the mains be sufficient?

Which currently available kit and CT sizes would you recommend for 20 A and 32 A branch circuits, and is the Home Assistant integration entirely local?

Are the kits sold in Belgium by Kermtstroomt suitable for this configuration, or would you recommend another EU supplier/setup?

An official confirmation of compatibility and the required components would help me avoid buying equipment that cannot accurately measure my electrical network

.

  1. Does the current IoTaWatt hardware support this exact 3 × 230 V delta/no-neutral supply for accurate active power and kWh measurements, including individual 230 V circuits connected across any of the three different phase pairs?

    Yes

  2. For each ordinary two-wire phase-to-phase branch circuit, is ONE CT on one conductor sufficient if the correct phase-pair reference is selected?

    Yes

  3. Can the derived-reference method use a single 230 V phase-to-phase voltage transformer in this situation? Which specific EU/Belgian-compatible voltage transformer(s) and setup would you recommend? Would direct voltage references be preferable?

    Yes a single can be used and is recommended. I can supply one if Kermtsroomt doesn’t have them. Virtually all three-phase installs are derived (one reference) .

  4. How many of the 14 CT channels would remain available if I also wanted to measure the total three-phase supply? Would two CTs on the mains be sufficient?

    The IoTaWatt supports 15 inputs, one of which must be a voltage reference. Two of the remaining 14 can be used as either a CT or VT input, so if you use derived reference (one VT) you will be able to configure 14 inputs. You can measure the mains using two CTs.

  5. Which currently available kit and CT sizes would you recommend for 20 A and 32 A branch circuits, and is the Home Assistant integration entirely local?

    You can use 50A CTs for those circuits but will probably need two 100A for your mains.
    There are several ways to import data to Home Assistant. The common integration is completely local as HA queries IoTaWatt on the local LAN.

  6. Are the kits sold in Belgium by Kermtstroomt suitable for this configuration, or would you recommend another EU supplier/setup?

    Those kits should be suitable. There are no other EU suppliers that I am aware of.