Questions from email

1 meter.

Not a problem, however the 120V kit does require you select at least two mains CTs. You can use the Generic kit if providing alternate CTs.

Yes, they are sideways so two will fit.

Not really. Conventionally, when you say “3 phase, 600 amp”, that would mean that each phase has a 600A capacity. That is also supported by your description of parallel cables for each phase. So, using 100A CTs is definitely not appropriate, and I doubt the 16mm 100A CTs would fit around the cables anyway.

In this situation, for each phase, you could use

  • 2x400A into 2 IoTaWatt inputs.
  • 2x600A combined with a splitter into 1 IoTaWatt input.
  • 2x400A combined with a splitter into 1 IoTaWatt input changing IoTaWatt burden resistor to 10 Ohm.
  • 1x600A with both cables running through it into one IoTaWatt input. The CT is 36mm opening so your incoming cable would need to be 18mm or less.
  • 1x600A Echun ECS55600 (special order 3-4 weeks) into one IoTaWatt input.

OK

Two ways to do that:

  • 2x100A CTs into two inputs with direct reference on each.
  • 1x100A CT into one input with derived reference. (You can still use direct reference for 120V circuits)

This is technically not a split-phase subpanel. It uses the same physical panel, but the phase of the 208V is not the same as the 120V phases. You have three different phases at play. That said, what you describe will monitor the sub-panel correctly.

Ditto