Seriously, this post is not the basis for a discussion, but I do want to debunk some of the misinformation.
I point the reader to this post from a couple of years ago:
To suggest that CTs may be +25%/-100% accurate is completely wrong for even the most low quality units. Reputable manufacturers typically produce CTs that are +/- 1% or as in the case of the AcuCTs +/- .5%. You would be hard pressed outside of a lab to find equipment capable of finer calibration. As a practical matter, field calibration is not possible, or for that matter, desirable or necessary.
Wire Size and Voltage have nothing to do with the current reading of the CT. If a #8 wire is carrying 10 amps in a 240V circuit, it will read the same as a #14 wire in a 120V circuit carrying 10 amps. Induction noise, except maybe when reading milliamps, is a second order factor at best.